Default repurposing a circuit panel

I often need a simple transfer switch for safe installation of a stand by generator.
What I do is use a suitably sized circuit panel and make up a lock out plate so only one power source can be applied at a time
circuit protection is provided by upstream breakers on both inputs.
The breakers in the panel are fed in reverse and are used as switches.
The load is connected to the normal input terminals of the panel. I also transfer any demand loads to this panel.
Note that when using the generator input the customer must turn off all heavy loads in his house panel but can selectively run any load his generator is capable of supporting by turning every thing else in the panel off.

In this case the main feed is a 200 amp panel in the shop with the house fed from a 100 amp breaker in the shop panel. There is also a freezer circuit in the shop which will be transferred to the 15 amp breaker in the transfer panel.
Attached Thumbnails
Click image for larger version

Name:	plate ifran.jpg
Views:	108
Size:	96.2 KB
ID:	142263   Click image for larger version

Name:	assembled ifran.jpg
Views:	130
Size:	97.5 KB
ID:	142264  
__________________
Life beats the alternative hands down.
Reply With Quote
  #2  
Old 11-23-2017, 09:24 PM
Ironman's Avatar
Ironman Ironman is offline
Iron Modification Investigator
 
Join Date: Feb 2008
Location: Warburg, Alberta, Canada
Posts: 11,671
Default

I like it, simple and effective
I'd like the idea better with a padlock hoop, to moron proof it.
__________________
Gerry
“After all, no one is stupid enough to prefer war to peace; in peace sons bury their fathers, and in war fathers bury their sons.”
Herodotus

Even duct tape can't fix stupid ... But it can muffle the sound. Attributed to Red Green
Reply With Quote
  #3  
Old 11-23-2017, 10:09 PM
terry lingle's Avatar
terry lingle terry lingle is offline
Something's Fishy ...
 
Join Date: Aug 2004
Location: Birch Island, BC, Canada
Posts: 4,595
Default

It is a transfer switch in a home environment there is little point in a padlock as the service panel is 3 feet away.
In an industrial environment I would never do this I would use top quality specified equipment simply because of the required paper trail. Also the service is likely to be 600 volts and three phase in that situation.

In a "normal" home service I have supplied a small panel for the demand loads
put a 40 amp breaker in the main panel wired to a standard range receptacle. the input to the demand panel is a full rated range cord not one of the new ones with a reduced neutral conductor. the generator feeds a second range receptacle. In normal use the demant panel in plugged into the service fed receptacle. for generator just move the plug over. I label both receptacles
"TURN FEED BREAKERS OFF BEFORE MOVING PLUG"
This system as is the above panel is intended to prevent back feeding the grid in case of power outages.

What amazes me is the number of double male ended cord that people have made to power there home then called because there generator keeps blowing the breaker when they do not turn off the main in the house panel.
Fortunately I have not heard of any hydro side events attributed to this but it could result in a manslaughter charge in the worst case.
__________________
Life beats the alternative hands down.
Reply With Quote
  #4  
Old 11-24-2017, 08:47 AM
Ironman's Avatar
Ironman Ironman is offline
Iron Modification Investigator
 
Join Date: Feb 2008
Location: Warburg, Alberta, Canada
Posts: 11,671
Default

Quote:
Originally Posted by terry lingle View Post
What amazes me is the number of double male ended cord that people have made to power there home then called because there generator keeps blowing the breaker when they do not turn off the main in the house panel.
Fortunately I have not heard of any hydro side events attributed to this but it could result in a manslaughter charge in the worst case.
I hope those linemen are using hot line protocol on a 'dead' line. It is incredibly dumb to feed power into a powerline transformer.
As long as someone who really knows everything about electricity doesn't unbolt the slider plate, what you have is a great option. I need to copy that.
__________________
Gerry
“After all, no one is stupid enough to prefer war to peace; in peace sons bury their fathers, and in war fathers bury their sons.”
Herodotus

Even duct tape can't fix stupid ... But it can muffle the sound. Attributed to Red Green
Reply With Quote
  #5  
Old 11-24-2017, 10:06 PM
rustythe4x4's Avatar
rustythe4x4 rustythe4x4 is offline
Elite Member
 
Join Date: Oct 2010
Location: Saskatchewan
Posts: 1,465
Default

I may have to copy it as well.
I have seen commercial units set up in a similar fashion. I wish I could remember where.

I have a transfer switch that uses back to back breakers tied together with a bar making it impossible to have both breakers on at the same time.
__________________
Living the country life


Learning boils down to "Repetition or the avoidance of pain", some people learn by doing, some by watching and some have to pee on the electric fence. - Norm W.

Mathew 10:36
And a man's foes shall be they of his own household
-Ironman quoting the Bible
Reply With Quote
  #6  
Old 11-24-2017, 10:32 PM
milomilo's Avatar
milomilo milomilo is offline
Auction Addict
 
Join Date: May 2010
Location: Wheatland, Wyoming
Posts: 12,090
Default

Quote:
Originally Posted by rustythe4x4 View Post
I may have to copy it as well.
I have seen commercial units set up in a similar fashion. I wish I could remember where.

I have a transfer switch that uses back to back breakers tied together with a bar making it impossible to have both breakers on at the same time.
I saw a home made one like that a few years ago and thought it was a pretty nifty way to do it.
__________________
Chris

“In order to become the master, the politician poses as the servant.” Charles de Gaulle
Reply With Quote
  #7  
Old 11-24-2017, 10:44 PM
terry lingle's Avatar
terry lingle terry lingle is offline
Something's Fishy ...
 
Join Date: Aug 2004
Location: Birch Island, BC, Canada
Posts: 4,595
Default

I have a set of linked breakers Here. They are pricey also the ones I have are both the same rating.
I would use them if the standby generator was capable of supplying the full load current. If that is not the case then two correct breakers and a panel will be less expensive
__________________
Life beats the alternative hands down.
Reply With Quote
  #8  
Old 11-25-2017, 11:58 PM
Lowe.Buuck Lowe.Buuck is offline
Newbie
 
Join Date: Jul 2017
Location: Minnesota, USA
Posts: 3
Default

Thanks for a timely post.

I just purchased a Honda EU2000I and am working out how to power a few selected loads in the house.

I have a 5000w, 6000w and 9500w generators and a suicide cord to back-feed the house from the shop. The house has a 200a breaker/disconnect box right below the meter. So I can use that and/or the main breaker in the panel to disconnect from the grid.

The issue I wanted to address is the fuel consumption and power quality of the larger generators. I only had $225 invested in all three, however they burn a lot of fuel and some electronics don't like the power quality.

I went through the house and measured the start and running watts of most of the loads in the house. The house needs less than 1000w of 120v in the winter to keep critical loads operating. The EU2000I in Eco mode will use a fraction of the fuel, is much quieter and produces clean power.

I'm still trying to figure the best way to get 120v to 5 locations in the house. I realize that if I back-feed 120v from the shop I will only power one side of the main panel.

I could turn off all the 240v breakers, and then feed the 120v hot leg to both sides of the main panel.

The house mostly has 2 wire service. I am considering wiring 5 new 120v grounded runs for critical loads (basically pre-wired extension cords) and have been trying to figure the best way to power them with the Honda.

My thought was a separate panel for these new circuits keeping them totally separate from the existing wiring.

I could also use your transfer switch to feed this panel from a 15a breaker in the main panel when the grid power is up.

Any suggestions?
Reply With Quote
  #9  
Old 11-26-2017, 12:28 AM
Samcord Samcord is offline
Elite Member
 
Join Date: Jun 2012
Location: Peoria
Posts: 1,689
Default

Quote:
Originally Posted by Lowe.Buuck View Post



I could turn off all the 240v breakers, and then feed the 120v hot leg to both sides of the main panel.







Any suggestions?

Can't you move the 5 circuits to the same leg?
Reply With Quote
  #10  
Old 11-26-2017, 12:47 AM
Samcord Samcord is offline
Elite Member
 
Join Date: Jun 2012
Location: Peoria
Posts: 1,689
Default

I wanted to make it simple and safe. I installed one of these. So easy a cave man could operate it. No worries about shutting unnecessary loads off. The top row of switches are three position - utility, off, generator.

You basically loop the circuits from the utility breaker, through the transfer switch, and then to the load. You have two wires from the transfer switch that you route into the breaker panel. You disconnect the house wire from the breaker, then connect one wire from the transfer switch to the breaker, and splice the other wire to the house wire. You also have a single larger wire for common.

If I'm not home when the power goes out, I'm confident that my wife could handle it.

They make smaller ones with fewer circuits. Click image for larger version

Name:	IMG_4687.JPG
Views:	44
Size:	140.5 KB
ID:	142296
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Web Search:

All times are GMT -5. The time now is 12:04 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2018, vBulletin Solutions, Inc.